Darkside wrote:
doug - evergreen park wrote:
He gave my AC a once over yesterday...thanks Darkside!
That was one of the more dramatic changes I've seen from a simple condenser cleaning...
Chus you'd appreciate... it's a 22 system, head pressure around 295, 2 to 4 degrees subcooling... I'm pretty sure theres other issues like minor noncondensibles and a possible liquid line or metering obstruction but when I just took the top off and ran the hose thru the condenser the head pressure dropped to around 195... still low on subcooling... 1.5 lbs or so added and I got around 10 subcooling at about 210 psi and suction line around 65 psi and 13 superheated.
Clean your condensers people.
I did a furnace and AC change out two years ago. Last summer, I get a call that the AC isn't working. They had just finished doing a ton of construction. His asshole carpenter just decided that he didn't need two of his returns, and blocked them off. He hadn't changed his filter in months, and the condenser coil was full of grass, leaves, and weeds. The pressure on the high side was through the roof.
But, when it wasn't working properly, his wife wants to blame me. This is why I have done any equipment jobs since. You need some duct work run, I'm your guy. You need a new furnace or AC, call somebody else, I don't need the headache.
Yeah man, rough. But me? I HATE tinning. Can't. Fucking. Stand. Tinning. I'm glad there's guys like you out there. Cause I hate tinning.